Author Topic: Anyone have experience with Onan Quiet Diesel Model 3.2 HDZAA-6508X3 generator?  (Read 5358 times)
Brian Diehl
Hero Member
*****
Offline Offline

Posts: 984




Ignore
« on: February 03, 2010, 02:55:56 PM »

Model 3.2 HDZAA-6508X3 Onan Quiet Diesel generator

http://www.cumminsonan.com/www/html/Common/pdf/specsheets/a-1501.pdf

I know this generator is only 26.7 amps @ 120v, but I think it would be perfect for what I want my bus to be able to do.  Has anyone had any experience with this generator?  It is much lighter than the full size RV generators and much smaller.  It will fit perfectly where I want it to go.  I am currently only wired for 30amps in my bus and have never had the need for more power.  So, I think this would handle what I want power for quite nicely.

Thoughts, opinions?  Is it good or bad?  Is it reliable?
Logged
John316
Hero Member
*****
Offline Offline

Posts: 3261

MCI 1995 DL3, DD S60, Allison B500.




Ignore
« Reply #1 on: February 03, 2010, 03:22:44 PM »

Brian,

Looks good to me. I would guess it would do just fine. However, are you looking at getting it new, or used? I have heard that you can't trust the Onans, like you can some of the others (Kubota's for example).

FWIW

God bless,

John
Logged

MCI 1995 DL3. DD S60 with a Allison B500.
edvanland
Sr. Member
****
Offline Offline

Posts: 360




Ignore
« Reply #2 on: February 03, 2010, 03:30:17 PM »

My experiance with Onan (junk) I would not touch one with a ten foot pole.
ED
Logged

Ed Van
MCI 7
Cornville, AZ
gumpy
Some Assembly Required
Hero Member
*****
Offline Offline

Posts: 3273


Slightly modified 1982 MC9


WWW

Ignore
« Reply #3 on: February 03, 2010, 04:03:58 PM »

Well, so far, I like mine. But then again, I have only put about 50 hours on it over 2 years.

BTW, when I started looking, I figured I could get by with 4KW, but I think 3.2KW would be pushing it a bit to run the basement air, even with augmentation by the inverter.
I couldn't find a 4KW. I ended up with 7.5Kw and it's just about perfect.

Your needs might require less, though. 

craig


« Last Edit: February 03, 2010, 04:06:33 PM by gumpy » Logged

Craig Shepard
Located in Minnesquito

http://bus.gumpydog.com - "Some Assembly Required"
rv_safetyman
Hero Member
*****
Offline Offline

Posts: 2199


Jim Shepherd


WWW

Ignore
« Reply #4 on: February 03, 2010, 04:34:41 PM »

Brian, Onan is, by far, the choice of most quality motorhome manufacturers.  That does not mean it is the best, but they would change if there was a big problem. 

The thing I would worry a bit about is that generators are de-rated for altitude. 

Folks have often recommended that you should go with the smallest generator that will do the job.  However, I think that is a pretty marginal capacity.

Jim
Logged

Jim Shepherd
Evergreen, CO
85 Eagle 10/Series 60/Eaton AutoShift 10 speed transmission
Somewhere between a tin tent and a finished product
Bus Project details: http://beltguy.com/Bus_Project/busproject.htm
Blog:  http://rvsafetyman.blogspot.com/
John316
Hero Member
*****
Offline Offline

Posts: 3261

MCI 1995 DL3, DD S60, Allison B500.




Ignore
« Reply #5 on: February 03, 2010, 05:20:22 PM »

Jim,

Interesting about getting the smallest possible. We went with a big one (20KW), because we didn't think we would regret the extra power. The diesel consumption chart is a graph. Basically if you pull 20KW, you will burn the most. Anyways, we figured we would burn more, having a bigger engine, even if we were pulling, oh say 60 amps, instead of 180 that we can handle. Turns out, it pretty much burns the same amount both ways, bigger engine less load, smaller engine bigger load.

Just the way I have understood it...

God bless,

John
Logged

MCI 1995 DL3. DD S60 with a Allison B500.
luvrbus
Hero Member
*****
Online Online

Posts: 12793




Ignore
« Reply #6 on: February 03, 2010, 05:21:44 PM »

Onan has by far the best service network, people I know that own them are happy with the service and performance.
Fwiw I found the independent  generator suppliers units about  impossible get service and parts on the road no one stocks their parts


good luck
Logged

Life is short drink the good wine first
Brian Diehl
Hero Member
*****
Offline Offline

Posts: 984




Ignore
« Reply #7 on: February 03, 2010, 05:29:01 PM »

Craig, you are right, 3.2 KW is marginal and I'm confident I could not run both AC compressors at 100 degrees outside.  However, it might just handle both compressors at 80 degrees outside.  Yes, marginal ... Good points worth contemplating and keeping in mind especially since my inverter is not capable of augmenting the generator.  I'm hoping Outback comes out with generator support someday!
Logged
belfert
Hero Member
*****
Offline Offline

Posts: 5448




Ignore
« Reply #8 on: February 03, 2010, 05:43:14 PM »

Onan, by far, has the most complaints, but they also have the majority of the RV market too.  A number of diesel pushers are starting to come with Powertech generators, but like Tom says the service will be harder to come by than for Onan.  Cummins has shops all over that also service Onan.
Logged

Brian Elfert - 1995 Dina Viaggio 1000 Series 60/B500 - 75% done but usable - Minneapolis, MN
TomC
Hero Member
*****
Offline Offline

Posts: 6862





Ignore
« Reply #9 on: February 04, 2010, 02:03:11 PM »

The problem with Onan or Kohler (the second largest genset maker) is that they make their own electronics, and you have to buy it from them.  Small independents like Powertech, Wrico International, etc uses universal electronics that are obtainable (many times) through normal parts stores, at a considerable reduction in price.  Practically all genset manufacturers use Kubota, Yanmar, Isuzu, etc and large alternator manufacturers like Seimans, etc.  But-you have to watch even that since I know that with the Onan Kubota powered 3 cylinder, the middle cylinder is different then the other two once again forcing you to buy expensive Onan parts.  Good Luck, TomC
Logged

Tom & Donna Christman. '77 AMGeneral 10240B; 8V-71TATAIC V730.
belfert
Hero Member
*****
Offline Offline

Posts: 5448




Ignore
« Reply #10 on: February 04, 2010, 02:13:31 PM »

I happen to have a Powertech Ultimate series generator.  I'm not entirely sure, but there appears to be at least one circuit board that would have to be ordered from Powertech if it blew. 

If it is better or worse than Onan I don't know.  Powertech does make a small generator about the same size as the Onan Brian is looking at, but the Powertech costs almost as much as what I paid for my 8KW model back in Fall 2006.  Powertech's prices in the past three years are through the roof.
Logged

Brian Elfert - 1995 Dina Viaggio 1000 Series 60/B500 - 75% done but usable - Minneapolis, MN
luvrbus
Hero Member
*****
Online Online

Posts: 12793




Ignore
« Reply #11 on: February 04, 2010, 02:44:13 PM »

Don't think for one minute you pick up Dick Wright's stuff off the shelf I have had one of his 13k generators before and he uses a special shut down I tried to buy one from Kubota before and finally had to have one shipped from him at 245.00 bucks



good luck
Logged

Life is short drink the good wine first
Fredward
Hero Member
*****
Offline Offline

Posts: 624


MC-5A #5401 8" roof raise 8V71 with MT647




Ignore
« Reply #12 on: February 04, 2010, 09:10:16 PM »

Brian,
You almost have two threads going here. Will a 3.2 kW do the trick and is an Onan quiet diesel any good. I don't know anything about the diesels, but I do know that 3,000 watts isn't very much. I've got a 7kW genset and most of the time its overkill. But it will run both roof airs when I need it. I've parked next to guys with the Onans and when they have control circuit problems; they don't work AT ALL. Remember the guy in the brand new coach next to me at Rollag two years ago? That was an Onan.

If most of what you're going to do is charge batteries and run some light duty electrical appliances, then I think a little 3.2 kW diesel might be nice. What RPM does it run at? I'm guessing 3600 ? It would be a little screamer.
Fred
Logged

Fred Thomson
viento1
Full Member
***
Offline Offline

Posts: 193



WWW

Ignore
« Reply #13 on: February 25, 2010, 10:48:55 PM »

What did you decide to do?

I have a onan quiet Deisel 10kw and it is big and heavy and I only use 30 amps anyway. I also noticed that my circuit breaker on the panel although rated for 30 amps can only handle about 28 for any length of time before switching off so I am on the same page as you. I could open up an entire bay (good for skiis, surfboards etc)
Logged

Ok, it's time to go on another road trip.
www.randalclark.com
MC5
Utahclaimjumper
Hero Member
*****
Offline Offline

Posts: 842




Ignore
« Reply #14 on: February 26, 2010, 02:52:56 AM »

My 7.5 quite diesel has 1700 trouble free hrs. and uses very little fuel due to a variable speed system.>>>Dan
Logged

Utahclaimjumper 
 EX 4106 (presently SOB)
Cedar City, Ut.
 72 VW Baja towed
bevans6
Hero Member
*****
Offline Offline

Posts: 4768


1980 MCI MC-5C




Ignore
« Reply #15 on: February 26, 2010, 05:03:53 AM »

Remember that circuit breakers are supposed to be loaded to no more than 80% of nominal on a continuous basis.  So 30 amps is 24 amps.  Continuous load is a steady load for over three hours, and heat is the issue.  Breakers are apparently rated at 104 degrees F in free air, and obviously all of mine  are in enclosed boxes right beside other heat sources.

Anyway, I have a Yamaha 3000 watt gas generator.  the choice was far more economics, size, and noise level than anything else, it runs my one AC unit and charges my batteries and lets me run my block heater when it's cold out.  But I have tripped the breaker on it, hence it is de facto too small.  But I knew that and accepted the energy management issues when I chose it, so I'm good with that.

I have a question about the big diesel generators.  Don't they offer some serious problems with noise and vibration?  they must have a fairly decent sized engine running there.

Brian
Logged

1980 MCI MC-5C, 8V-71T from a M-110 self propelled howitzer
Spicer 8844 4 speed Zen meditation device
Vintage race cars -
1978 Lola T440 Formula Ford
1972 NTM MK-4 B/SR
JackConrad
Orange Blossom Special II
Global Moderator
Hero Member
*****
Offline Offline

Posts: 4447


73' MC-8 8V71/HT740 Southwest Florida


WWW
« Reply #16 on: February 26, 2010, 05:26:55 AM »

    Not sure what you consider "BIG", but I can tell you about the PowerTech line (the only brand I am familiar with).  Last time I was at their place, several years ago, the 10 & 12 KW use a 4 cylinder kubota diesel engine.  They were using a turbocharged 4 cylinder on the 17 & 20 KW. The smaller 7 & 8 KW use a 3 cylinder kubota.
   Noise level varies a lot depending on location, baffling, and sound insulation.  Vibration can also vary depending on mounting differences.
   Compared to our old gas Onan 6.5, our PowerTech 9 KW (10KW head on a 3 cylinder Kubota) is quieter but a slight vibration that I feel through the bus floor.  Jack
Logged

Growing Older Is Mandatory, Growing Up Is Optional
Arcadia, Florida, When we are home
http://s682.photobucket.com/albums/vv186/OBS-JC/
luvrbus
Hero Member
*****
Online Online

Posts: 12793




Ignore
« Reply #17 on: February 26, 2010, 05:42:46 AM »

My diesel generator is quite and I use no muffler but like Jack I had some vibration till I removed it from the slideout with air bags and installed jell bags.
A slideout will transfer vibration but the way some generators are installed it is a must but I remote mounted all my filters and did away with the slide and I am very happy with the results.



good luck
« Last Edit: February 26, 2010, 06:21:21 AM by luvrbus » Logged

Life is short drink the good wine first
usbusin
Hero Member
*****
Offline Offline

Posts: 508


'60 PD4104-4355(sold) Now Freightliner Conversion




Ignore
« Reply #18 on: February 26, 2010, 06:04:37 AM »

luvrbus, what are "jell bags" and where can I see the specs on them?  My 8kw Powertech Kubota transfers  vibration through the factory mounts and I'd like to eliminate the vibration if the jell bags are not too thick as I don't have a lot of vertical clearance.  Let us know where the specs can be located.  Thanks so much.
Logged

Gary D

USBUSIN was our 1960 PD4104 for 16 years Ustruckin' is our 2001 Freightliner truck conversion
luvrbus
Hero Member
*****
Online Online

Posts: 12793




Ignore
« Reply #19 on: February 26, 2010, 06:38:36 AM »

Gary, I bought mine from West Marine 2 in thick x 3 1/2 in round 2 bolts on the bottom and a stud on the top.
They are a little pricey over 200 bucks for 4 my understanding Dick Wright sell the jell bags now.


good luck
Logged

Life is short drink the good wine first
belfert
Hero Member
*****
Offline Offline

Posts: 5448




Ignore
« Reply #20 on: February 26, 2010, 07:09:03 AM »

   Not sure what you consider "BIG", but I can tell you about the PowerTech line (the only brand I am familiar with).  Last time I was at their place, several years ago, the 10 & 12 KW use a 4 cylinder kubota diesel engine.  They were using a turbocharged 4 cylinder on the 17 & 20 KW. The smaller 7 & 8 KW use a 3 cylinder kubota.
  

Powertech also used the Cat (Perkins) engine too for the smaller 8KW generators at one point.  They offered a choice of either when I bought my unit.  I would have choosen the Kubota, but they only had a Cat in stock.  It appears they no longer offer the Cat engine.  This was back in 2006 and at the time I was pushing hard to leave in under 6 weeks so I needed a genny right now.  (It turns out I never went anywhere that year due to other issues.)
Logged

Brian Elfert - 1995 Dina Viaggio 1000 Series 60/B500 - 75% done but usable - Minneapolis, MN
TomC
Hero Member
*****
Offline Offline

Posts: 6862





Ignore
« Reply #21 on: February 26, 2010, 09:28:48 AM »

Powertech makes a really neat 8kw compact generator with built in squirrel cage blower.  This is the exact unit that a friend of mine had on his big rig truck with ARI sleeper that had 23,000 hours on it when it was sold. On the engine, he replaced one water pump, and had the alternator end rebuilt once-not bad!.  Good Luck, TomC
Logged

Tom & Donna Christman. '77 AMGeneral 10240B; 8V-71TATAIC V730.
usbusin
Hero Member
*****
Offline Offline

Posts: 508


'60 PD4104-4355(sold) Now Freightliner Conversion




Ignore
« Reply #22 on: February 26, 2010, 09:37:47 AM »

Thanks, luvrbus I'll check them out.
Logged

Gary D

USBUSIN was our 1960 PD4104 for 16 years Ustruckin' is our 2001 Freightliner truck conversion
Utahclaimjumper
Hero Member
*****
Offline Offline

Posts: 842




Ignore
« Reply #23 on: February 26, 2010, 12:41:46 PM »

My 7.5 quite onan is 60 decibells at ten feet and NO vibs.>>>Dan PS: left it running all night the last time out because didnt know it was running!!
Logged

Utahclaimjumper 
 EX 4106 (presently SOB)
Cedar City, Ut.
 72 VW Baja towed
gus
Hero Member
*****
Offline Offline

Posts: 3527





Ignore
« Reply #24 on: February 26, 2010, 06:20:00 PM »

Save yourself a bunch of $$ and weight and get a gas, water cooled, quiet, smooth 6KW Honda EV6010.

The only down side is you have to construct your own box, the side clearances for incoming cooling are are critical, and you need a separate gas tank. However, the results are worth it.

Don't get caught up in this myth that 3600rpm gensets are no good, it makes absolutely no difference what the rpms are, what counts is smoothness.
Logged

PD4107-152
PD4104-1274
Ash Flat, AR
Brian Diehl
Hero Member
*****
Offline Offline

Posts: 984




Ignore
« Reply #25 on: February 26, 2010, 08:00:03 PM »

What does a decent Honda go for?
Logged
luvrbus
Hero Member
*****
Online Online

Posts: 12793




Ignore
« Reply #26 on: February 26, 2010, 08:22:12 PM »

Brian, I am not telling not to buy a Honda it is your money I do work on those sometimes and parts are very expensive for the EV6010 here are some prices on replacement parts I have bought then you can make up your own mind and they were generators with 1500 or less hours

radiator        500.00 and shops will not repair one
coil              100.00
fuel pump      150.00
fan              200.00
water pump   125.00
voltage reg   350.00   


good luck
Logged

Life is short drink the good wine first
gus
Hero Member
*****
Offline Offline

Posts: 3527





Ignore
« Reply #27 on: March 02, 2010, 03:26:03 PM »

Those prices are truly a shock but maybe not in comparison with some of the Onan prices from Cummins I've seen posted.

Good thing I didn't see these before I bought it because I'm cheap!

It cost around $4200 including the muffler kit and shipping. You also have to build the box.
Logged

PD4107-152
PD4104-1274
Ash Flat, AR