Author Topic: Defeating GFI  (Read 1628 times)
Sean
Geek.
Hero Member
*****
Offline Offline

Posts: 2553


'85 Neoplan Spaceliner "Odyssey"


WWW

Ignore
« Reply #30 on: August 28, 2014, 10:40:42 AM »

If the GFCI in question is working properly, then any ground-neutral fault in the coach would trip it instantly.  The fact that it is not tripping instantly means that either it is inoperative, or else you don't really have such a fault in your coach.  Step one here would be to test the GFCI.  The self-test button is unreliable; instead, purchase a GFCI tester -- this is one of those little three-light testers that also tell you if the outlet is properly wired, except that it also has a little button you press to test the GFCI.  Available at Home Depot and elsewhere, they are maybe $15.  Handy to have, because you can never tell when a plain-looking outlet might be wired downstream of a GFCI, and this lets you know right away.

Now, having said all of that, my experience is that GFCI outlets that nuisance-trip after a period of time (as opposed to when you first plug in) are also defective.  One common issue is moisture in the J-box, which can become just conductive enough to cause a trickle current between either the hot or the neutral and the ground.  When you think about it, moisture is exactly one of the reasons GFCI outlets are so important in the first place.

If your coach is tripping this one outlet consistently after a period of time, I would not implicate the coach itself unless is also does that consistently to other GFCI outlets.  If you can't find another outlet nearby to test, then drop the $20 and replace your host's receptacle for him, and see if the problem goes away.  We carried a spare GFCI with us for exactly this reason.  (We also carried spare 50- and 30-amp breakers for defective campground pedestals, along with spare receptacles.  When you get the last good spot at that remote state park, it's easier to just fix the dang pedestal than to move or try to get rangers or volunteer hosts to do anything about it.)

HTH,

-Sean
Logged

Full-timing in a 1985 Neoplan Spaceliner since 2004.
Our blog: http://OurOdyssey.BlogSpot.com
wagwar
Full Member
***
Offline Offline

Posts: 178


WWW

Ignore
« Reply #31 on: August 28, 2014, 02:04:03 PM »

It does not trip instantly, until I flip one of my breakers in the bus on (eg entry door receptacle). Recall that I have all of my breakers off. With all breakers off the gfi will pop after a few minutes of charging- even at a low 5a level. If I flip a breaker on, that will cause it to pop immediately. So, still not able to definitively rule out neutral ground bond or ground fault problem.

Logged

wagwar
Full Member
***
Offline Offline

Posts: 178


WWW

Ignore
« Reply #32 on: August 28, 2014, 02:07:35 PM »

Btw, I can confirm that neutral and ground are not bonded in main panel, so if it is a neutral ground bond problem, it is not happening at my main panel.
Logged

robertglines1
steam nut
Hero Member
*****
Offline Offline

Posts: 4008





Ignore
« Reply #33 on: August 28, 2014, 05:00:17 PM »

Pro already been mentioned--Grounds bonded within some appliance.  Been there on that one.
Logged

Bob@Judy  98 XLE prevost with 3 slides --Home done---last one! SW INdiana
Seangie
www.herdofturtles.org
Hero Member
*****
Offline Offline

Posts: 864


And We're Off... Like a Herd of Turtles


WWW

Ignore
« Reply #34 on: August 31, 2014, 09:22:10 AM »

Dave (wagwar) -

How did you make out?  Any progress?

-Sean
Logged

'Cause you know we,
we live in a van (Eagle 10 Suburban)
Driving through the night
To that old promised land'
wagwar
Full Member
***
Offline Offline

Posts: 178


WWW

Ignore
« Reply #35 on: August 31, 2014, 08:21:30 PM »

Not really. I swapped out the gfi for standard rec. temporarily. I need to thoroughly test the neutral ground bond for proper operation, but I just don't know how to go about it. 
 
The tests that Sean outlined in the previous thread that I linked to in a previous response seem to check out ok. So I'm not sure where to go from here. I think i may still have a problem.

Logged

Lin
Hero Member
*****
Offline Offline

Posts: 4558

1965 MC-5a




Ignore
« Reply #36 on: August 31, 2014, 10:06:25 PM »

Just a question.  Would using one of those little 3 prong to 2 prong adaptors have worked since it cuts out the ground?
Logged

You don't have to believe everything you think.
bobofthenorth
Hero Member
*****
Offline Offline

Posts: 2082



WWW

Ignore
« Reply #37 on: September 01, 2014, 11:16:26 AM »

Just a question.  Would using one of those little 3 prong to 2 prong adaptors have worked since it cuts out the ground?

Sometimes. Yes. But. ........

If the ground fault is a connection between the ground and neutral (green/white) on the coach then the 3 to 2 adapter will let you hook up.  Whatever you have for a ground fault still exists - you've just masked its effect.

If the ground fault is an alternative path to ground - ie. not through the green wire - then the 3 to 2 adapter won't change anything. 

I can think of situations where the 3:2 adapter might be an acceptable risk --  FOR ME --- but I can also remember homes that were wired with only 2 conductors.  We don't do that anymore either.

Ultimately this comes in the category of "if you have to ask the question then you shouldn't try it at home".

Logged

R.J.(Bob) Evans
1981 Prevost 8-92, 10 spd
My website
Our weblog
Simply growing older is not the same as living.
Jriddle
Hero Member
*****
Offline Offline

Posts: 667





Ignore
« Reply #38 on: September 01, 2014, 05:51:02 PM »

Sometimes. Yes. But. ........

If the ground fault is a connection between the ground and neutral (green/white) on the coach then the 3 to 2 adapter will let you hook up.  Whatever you have for a ground fault still exists - you've just masked its effect.

If the ground fault is an alternative path to ground - ie. not through the green wire - then the 3 to 2 adapter won't change anything. 

I can think of situations where the 3:2 adapter might be an acceptable risk --  FOR ME --- but I can also remember homes that were wired with only 2 conductors.  We don't do that anymore either.

Ultimately this comes in the category of "if you have to ask the question then you shouldn't try it at home".



I remember living in a trailer house that was wired by a friend. Every time it rained we would get shocked when the door  was opened from the outside. I guess we are lucky to be around to tell the story. You must ensure you don't become the ground for a ground fault. I guess at that time nothing would hurt me LOL. Young dump and ______?

John
Logged

If It Can't Be Grown Then It Has To Be Mined
John Riddle
Wells NV
1984 MC9