Author Topic: All 3 roof airs failed simultaneously?  (Read 4041 times)
plyonsMC9
Global Moderator
Hero Member
*****
Offline Offline

Posts: 1159


Big Wheels Turnin'


WWW
« on: April 20, 2008, 06:47:52 PM »

Greetings fellow busnuts!

Well, finally some time up north with good weather and no salt on the roads.  So, out came our bus.  Throttle/cable stuck a little.  Took care of that. 

Only real problem? Bus was fine - but ALL 3 of my roof air conditioners do not function. 

Symptom is the same on all 3.  The fan will not start on any of them.  I did not use the a/c's during the winter.  Compressors run, I guess.  Just a humming sound.  When I turn just the fan on, I hear a quieter hum.  Each a/c is on a separate breaker.  At first I thought it may be a problem with the generator, but I plugged the coach into a shore 50 amp circuit.  Same symptoms. 

My panel voltage meeters show 122 volts.  All lights, refrigerator, portable heaters, etc., function w/o any problem.  Two of the a/c breakers are on one leg, the other a/c breaker is on the other leg.

a/c breakers also trip / spark now.

Where do I start on something like this?  Help! 

Thanks! Phil
« Last Edit: April 21, 2008, 12:05:27 PM by plyonsMC9 » Logged

Northern Arizona / 1983 - MC9
luvrbus
Guest

« Reply #1 on: April 20, 2008, 06:51:06 PM »

 Phil take the covers off the top on the roof and free the fans on top happen to me before on a S&S  good luck
Logged
coachconverter
Full Member
***
Offline Offline

Posts: 211



WWW

Ignore
« Reply #2 on: April 20, 2008, 06:54:08 PM »

Sounds like the fan motors have locked up.  I would try to spin them manually, then lube them up. 
Logged
JohnEd
Hero Member
*****
Offline Offline

Posts: 4571




Ignore
« Reply #3 on: April 20, 2008, 06:55:27 PM »

Had this happen with one once.  The squirrel cage was "stuck".  Take down the inside shroud/defuser/filter.  Look up in there and see the sq. fan rotor.  Make sure it spins freely.  DON"T leave it in the "ON" posit for long or you will burn up the motor. Shocked  LOW AC will do this so check you ac volts when you try the AC.  Do they act the same in generator mode?

You will get this one soon. Wink  The really bad ones are easy. Cool  Now if you had a sit where only one would work on odd numbered Tuesdays.....then that would be significant. Grin

John
Logged

"An uneducated vote is a treasonous act more damaging than any treachery of the battlefield.
The price of apathy towards public affairs is to be ruled by evil men." Plato
We can easily forgive a child who is afraid of the dark; the real tragedy of life is when men are afraid of the light.
Pla
plyonsMC9
Global Moderator
Hero Member
*****
Offline Offline

Posts: 1159


Big Wheels Turnin'


WWW
« Reply #4 on: April 20, 2008, 06:57:41 PM »

Thanks guys!  I will (carefully) get up on the roof, remove covers, spin the fans.  Is it easy to lube the motors?  I will post back with my progress during the week.  Breakers are OFF to all three units right now. 

Kind Regards, Phil
Logged

Northern Arizona / 1983 - MC9
Sean
Geek.
Hero Member
*****
Offline Offline

Posts: 2536


'85 Neoplan Spaceliner "Odyssey"


WWW

Ignore
« Reply #5 on: April 20, 2008, 07:00:19 PM »

Phil,

It's possible, as luvrbus and others wrote, that the motor shafts are bound up, and spinning them by hand will free them.  (If that does turn out to be the problem, you can avoid it in the future by running all your units for a few minutes each month, even in the winter.  About five minutes should be sufficient to circulate the refrigerant and its entrained lubricating oil.)

That said, I find it strange that this would happen to all units simultaneously.

I would pop the ADB or duct cover off each unit and test the power right at the unit with a voltmeter.  It's possible you have some common failure, such as a neutral bus issue.

Another thing you can try is to get a heavy-duty extension cord of suitable length, whack the receptacle off the end, and wire it directly to one of the units (disconnecting the unit from its hard-wire source, of course), then plug that into a known good shore-side receptacle, and see what happens.

Let me know where that gets you and we can take it from there.

-Sean
http://OurOdyssey.BlogSpot.com
« Last Edit: April 20, 2008, 07:01:53 PM by Sean » Logged

Full-timing in a 1985 Neoplan Spaceliner since 2004.
Our blog: http://OurOdyssey.BlogSpot.com
plyonsMC9
Global Moderator
Hero Member
*****
Offline Offline

Posts: 1159


Big Wheels Turnin'


WWW
« Reply #6 on: April 20, 2008, 07:18:23 PM »

Hi Sean,

Cover is already off one of the units.  This will be e-z for me to test.  Also have a cord with the end wacked off coincidentally.  Nothing at all to do with my electric shrub trimmer getting out of control with my outdoor extension cord of course.   Cheesy   Yes, unusual that it would happen to all 3.  Normally I keep the a/c covers on all winter, but this year, I got iced before I could get them on, and I don't dare go on the roof w/ ice up there, so I decided to forego the a/c covers this year.

Kind Regards, Phil
Logged

Northern Arizona / 1983 - MC9
Nick Badame Refrig/ACC
1989, MCI 102C3, 8V92T, HT740, 06' conversion FMCA# F-27317-S "Wife- 1969 Italian/German Style"
Global Moderator
Hero Member
*****
Offline Offline

Posts: 4857


Nick & Michelle Badame


WWW
« Reply #7 on: April 20, 2008, 07:24:14 PM »

Hi Phil,

The guy's covered everything that I would have started you from. Thanks Guy's!

The only other thing I can add is if this turns out to be your problem, get some oil on the shaft ends up close the the bearings.

Even though you have sealed bearings, it will still seep somewhat into the seals.

Good Luck
Nick-
Logged

Whatever it takes!-GITIT DONE! 
Commercial Refrigeration- Ice machines- Heating & Air/ Atlantic Custom Coach Inc.
Master Mason- Cannon Lodge #104
https://www.facebook.com/atlanticcustomcoach
www.atlanticcustomcoach.com
jeffacc
Newbie
*
Offline Offline

Posts: 26


1983 MC9




Ignore
« Reply #8 on: April 20, 2008, 07:30:32 PM »

Hi Phil
   If the fans are not bound up check the capacitors you will need a meter that is cabable of reading microfarad as for starting the units in winter don't do it you will take the valves out in the compressors check with your manual for operating temps good luck.
                                                             Jeff
Logged
jok
Full Member
***
Offline Offline

Posts: 165


Its a bus thing...Im glad were on board!




Ignore
« Reply #9 on: April 20, 2008, 08:19:23 PM »

Hi Phil,

I'm in S.W. Michigan and am enjoying the great weather you guys are sending us. Keep it coming. Smiley

I have three Dometic Duo-Therms that had a similar failure. When I installed mine I wired all three to a Duo-Therm Comfort Control Center. The three are controlled by normal household phone lines, and they are tied together. I had to use a "in-line coupler" to tie them together. The "coupler" was low quality. When I had the failure I followed the "phone lines" and when I wiggled the front "coupler" all three came to life. I replaced the coupler and they have worked fine.

I also have blown the fuse that is under the cover (on the roof). I am glad I installed a sunroof to get on the roof.

Good luck,
John
« Last Edit: April 21, 2008, 07:51:07 AM by jok » Logged

1990 Prevost
1977 MC8-Sold
Southwest Michigan
belfert
Hero Member
*****
Offline Offline

Posts: 5391




Ignore
« Reply #10 on: April 20, 2008, 08:26:26 PM »

I think Phil is confusing A/C covers sometimes used in the winter for the plastic shrouds.  To get to the fan motors will require removing either the inside covers or the outside plastic shroud.

I also highly doubt all three fans locked up at once.
Logged

Brian Elfert - 1995 Dina Viaggio 1000 Series 60/B500 - 75% done but usable - Minneapolis, MN
FloridaCliff
Hero Member
*****
Offline Offline

Posts: 2458


"The Mighty GMC"




Ignore
« Reply #11 on: April 20, 2008, 08:29:09 PM »

Phil,

Don't know what kind of units you have, but my Coleman units require a 12 vdc control voltage to work.

If you have the same or similar, maybe a a fuse blew or wire disconnected over the Winter.

Cliff
Logged

1975 GMC  P8M4905A-1160    North Central Florida

"There are basically two types of people. People who accomplish things, and people who claim to have accomplished things. The first group is less crowded."
Mark Twain
Dreamscape
Guest

« Reply #12 on: April 21, 2008, 09:33:06 AM »

Phil, What did you come up with?

Did you check voltage at each unit as it goes in?

Critters maybe chewed some wires?

Let us know.

Paul
Logged
plyonsMC9
Global Moderator
Hero Member
*****
Offline Offline

Posts: 1159


Big Wheels Turnin'


WWW
« Reply #13 on: April 21, 2008, 10:08:39 AM »

Thanks Paul,

Tonight when I get home from work I will take some readings, check voltage, and post results!!  I'm very curious about this.  I really appreciate all the feedback & excellent suggestions.  Initially when something like this happens, it can be intimidating, but - NOT with the best busnuts in the world helping ya out!   Grin  Grin

Kind Regards, Phil

Logged

Northern Arizona / 1983 - MC9
plyonsMC9
Global Moderator
Hero Member
*****
Offline Offline

Posts: 1159


Big Wheels Turnin'


WWW
« Reply #14 on: April 21, 2008, 10:09:37 AM »

Phil,

Don't know what kind of units you have, but my Coleman units require a 12 vdc control voltage to work.

If you have the same or similar, maybe a a fuse blew or wire disconnected over the Winter.

Cliff

Hi Cliff, pretty sure they are Dometic low profile.  I'll check tonight for any kind of 12 vdc wires.

Thanks! Phil
Logged

Northern Arizona / 1983 - MC9