So I have been wrestling with this 34 year old Winnie that has been turning black with mildew out behind the barn...so to speak.  Getting down to the short strokes and want to bring back the OTR AC.  You know it is a R12 system cause the last time I used her they hadn't invented 134.  Well I have been of on a scavenger hunt for all my components and a replacement for the venerable York compressor.  Talked to more than a few "experts" in the trade.  I have acquired a really large condenser and a dryer and little more than info beyond that.  I finally called a shop across town and asked about getting all new houses cause 134 goes thru F12 rated stuff.  The nice man asked why I was converting and I told him I had no problem with the system at all except that it leaked down over the winter.  Every winter!  Wasn't a problem when R12 was cheap and I didn't understand about the ozone.  Now I have concerns.  AC guy said he would pressurise my system with a trace of R12 and nitrogen and find the point of leak and maybe we could repair the system instead of going to the expense of ripping it out.  He seemed to be on my side...remarkable.  I told him I had 4 cans of R12 from days gone by and he estimated I would need 60 to 120 dollars worth more max, if any, and he could provide it.  Now isn't that a happy ending?  Course it isn't over till the Fat Lady sings and I get frosty.

Did you know you can have a R12 system repaired in this day and age?  I will have it pumped down before I junk the old girl next year.

John

Logged

"An uneducated vote is a treasonous act more damaging than any treachery of the battlefield.
The price of apathy towards public affairs is to be ruled by evil men." Plato
“We can easily forgive a child who is afraid of the dark; the real tragedy of life is when men are afraid of the light.”
—Pla
Nick Badame Refrig/ACC
1989, MCI 102C3, 8V92T, HT740, 06' conversion FMCA# F-27317-S "Wife- 1969 Italian/German Style"
Global Moderator
Hero Member
*****
Offline Offline

Posts: 4874


Nick & Michelle Badame


WWW
« Reply #1 on: October 23, 2008, 06:54:00 PM »

Hi John,

You don't have to use R-12 and you don't have to retrofit to R134A either. There is a direct drop-in replacement gas for R12 that uses the same oil,

TX valves, and hoses. It's called R-409A. A blended gas with very close chactoristics as R-12. The most notable differences are in charging the system.

For an R-12 to R-409A retrofit, with a system that uses a TXV , you should use approximately 85 - 90 % of the charge weight for R-409A that was

originally used with R-12. When running at steady state conditions, you can expect to see suction pressures very similar to what the system ran at with

R-12. The discharge pressure will typically be 15 - 25 psi higher than it was with R-12.

To determine if the system is charged properly, you also want to check your superheat and subcooling. The best way to determine what the values of

superheat and subcooling should be for your system with R-12 is to contact the OEM. The values of superheat and subcooling that you should expect to see

with R-409A will be similar to those used for R-12. Once the system charge and other settings have been optimized, and the system is running at steady

state conditions, there may or may not be trace amounts of bubbles in the sight glass.

Good Luck
Nick-


Logged

Whatever it takes!-GITIT DONE! 
Commercial Refrigeration- Ice machines- Heating & Air/ Atlantic Custom Coach Inc.
Master Mason- Cannon Lodge #104
https://www.facebook.com/atlanticcustomcoach
www.atlanticcustomcoach.com
JohnEd
Hero Member
*****
Offline Offline

Posts: 4571




Ignore
« Reply #2 on: October 23, 2008, 08:03:10 PM »

Nick,

That is great news.

Thanks,

John
Logged

"An uneducated vote is a treasonous act more damaging than any treachery of the battlefield.
The price of apathy towards public affairs is to be ruled by evil men." Plato
“We can easily forgive a child who is afraid of the dark; the real tragedy of life is when men are afraid of the light.”
—Pla
jjrbus
Hero Member
*****
Offline Offline

Posts: 2313

MCI5C/N Ft Myers FL




Ignore
« Reply #3 on: October 24, 2008, 07:48:43 AM »

 With the cost and inconvienance of repairs plus the age of the compnents and you are getting rid of Winnie next year. Might you be better off running the genset and useing the roof air?

                                                                       Jim
Logged

Remember, even at a Mensa convention someone is the dumbest person in the room!

http://photobucket.com/buspictures

http://photobucket.com/buspictures
TomC
Hero Member
*****
Offline Offline

Posts: 6854





Ignore
« Reply #4 on: October 24, 2008, 09:50:39 AM »

Nick- do you have to completely evacuate the system to switch to the R409A, or can it be used as a topper?  Can R12 and R409A be mixed?  And can we as mere mortals buy R409A over the counter like we can with R134A?  Sort of important to be able to "top" off the system when on the road.  Even with the cost of switching to R134A, it maybe less in the long run since most auto parts stores sell the 1lb cans of R134A like they used to with R12.  Good Luck, TomC
Logged

Tom & Donna Christman. '77 AMGeneral 10240B; 8V-71TATAIC V730.
JohnEd
Hero Member
*****
Offline Offline

Posts: 4571




Ignore
« Reply #5 on: October 24, 2008, 11:54:09 AM »

Tom,

I keep my cars a good long while.  10 years min and I don't buy new but I have two and sometimes three cars on the road at any given point in time.  I have only had one car serviced for low freon and the Winnie.  AC seems to be a good reliable system...in general.  If I were to switch to "any" freon I would expect to never revisit that issue in the two years she has to live.  Expense is the driving factor for me but it goes without saying that it "must" operate.  People I have talked to, Nick included, have confirmed that 134 is not as effective as R12.  Maybe efficient is a more proper word.  Some that converted to 134 found that their AC system was no longer adequate.  I guess it is if the system is designed for the application but I understand that the condenser and evap and compressor are much larger than an equal tonnage R12 system.  My R12 system was really powerful so I thought I might be able to take the performance hit and still be adequate.  Then I got into the differences in the the two systems from the hardware system requirements and I lost confidence.  Seems that all the rubber hoses need to be replaced in a system as old as mine so I opted to rebuild/replace the old system.  I had been told by HVAC savvy people more than a few times over the years that I "couldn't" use 409 and they were good guys all and I can only surmise that by "you" they meant me personally because it takes a HVAC licence to squirt 409 around and not that the systems are not compatible.  If I can get the same performance from 409 as I did from R12 I will definitely go that way.

Thank you all for your interest and comments....especially you Nick,

John headed for cool.
Logged

"An uneducated vote is a treasonous act more damaging than any treachery of the battlefield.
The price of apathy towards public affairs is to be ruled by evil men." Plato
“We can easily forgive a child who is afraid of the dark; the real tragedy of life is when men are afraid of the light.”
—Pla
Nick Badame Refrig/ACC
1989, MCI 102C3, 8V92T, HT740, 06' conversion FMCA# F-27317-S "Wife- 1969 Italian/German Style"
Global Moderator
Hero Member
*****
Offline Offline

Posts: 4874


Nick & Michelle Badame


WWW
« Reply #6 on: October 24, 2008, 01:27:16 PM »

Nick- do you have to completely evacuate the system to switch to the R409A, or can it be used as a topper?  Can R12 and R409A be mixed?  And can we as mere mortals buy R409A over the counter like we can with R134A?  Sort of important to be able to "top" off the system when on the road.  Even with the cost of switching to R134A, it maybe less in the long run since most auto parts stores sell the 1lb cans of R134A like they used to with R12.  Good Luck, TomC

Hi Tom,
Yes, you would need to evacuate the system of R-12. But, only because the presure chactoristics will change your readings
if you are trying to get it right. R-409A is a little more expensive then 134 but still waaay cheaper then R12. i have not seen
it in small cans like 134 but most Refrigeration guy's like myself have the 30lb bottels.
Good Luck
Nick-
Logged

Whatever it takes!-GITIT DONE! 
Commercial Refrigeration- Ice machines- Heating & Air/ Atlantic Custom Coach Inc.
Master Mason- Cannon Lodge #104
https://www.facebook.com/atlanticcustomcoach
www.atlanticcustomcoach.com
RTS/Daytona
Hero Member
*****
Offline Offline

Posts: 526


Pete RTS/Daytona ->'89 TMC 35' 102" 6V92TA 4:10


WWW

Ignore
« Reply #7 on: October 24, 2008, 03:03:48 PM »

If anyone is interested

I have a 30 lb bottle of R12 - It now weights 11 lbs

not sure what the container weights - but-

It's $50 - I'm near Daytona Florida - just a few minutes from I-95

Pete ...386..672..0571... 

Come and get it !!!!

sorry - don't think I'll be at Arcadia this year
Logged

If you ain't part of the solution, then you're part of the problem.
lloyd
Jr. Member
**
Offline Offline

Posts: 74





Ignore
« Reply #8 on: October 24, 2008, 05:51:28 PM »

JFYI In British Columbia the only replacement for R 12 is R134a. It is against the law the charge a system with any ozone depleting substance. Saying that you can buy off the shelf "Artic chill" I think that is what is called, which has htdocarbons, propane? We can not use R12 at all either ertro fit or drain and leave empty
Lloyd
Logged
JohnEd
Hero Member
*****
Offline Offline

Posts: 4571




Ignore
« Reply #9 on: October 25, 2008, 12:26:19 AM »

RTS,

Stop that!  It is against fed reg to sell or buy R12 unless you are licensed as a HVAC and have the R12 ticket punched.  Beside that, it sells for much more than $50 a "pound" so you are giving away a valuable commodity. 

I hope you get email from off line and maybe drop Nick a PM and get his advice.  I am sure he wouldn't risk his licence, name or a fine but he most probably will have some private advice.

HTH,

John the worrier
Logged

"An uneducated vote is a treasonous act more damaging than any treachery of the battlefield.
The price of apathy towards public affairs is to be ruled by evil men." Plato
“We can easily forgive a child who is afraid of the dark; the real tragedy of life is when men are afraid of the light.”
—Pla
RTS/Daytona
Hero Member
*****
Offline Offline

Posts: 526


Pete RTS/Daytona ->'89 TMC 35' 102" 6V92TA 4:10


WWW

Ignore
« Reply #10 on: October 25, 2008, 06:17:20 AM »

Hey John

I no longer have a need for the r12

Just wanted to help any local Bus Nut out

So - why don't you just KMRA !!  (KISS MY ROYAL A$$ !!)

Pete RTS/daytona
« Last Edit: October 25, 2008, 10:55:08 AM by RTS/Daytona » Logged

If you ain't part of the solution, then you're part of the problem.
boogiethecat
Hero Member
*****
Offline Offline

Posts: 634



WWW

Ignore
« Reply #11 on: October 25, 2008, 09:00:08 AM »

FWIW you can sell R 12 all day and night without having any license. You just can't BUY it without a license.  The requirement is that the seller must verify that the buyer is certified and licensed to own and handle the stuff, or not sell it to him.  That's all...
Logged

1962 Crown
San Diego, Ca
JohnEd
Hero Member
*****
Offline Offline

Posts: 4571




Ignore
« Reply #12 on: October 25, 2008, 03:24:15 PM »

Boogie,

I haven't read any HVAC regs ever.  I was told "buy or sell" by two different auto AC shop owners and I wasn't selling or trying to buy anything, just BSing and visiting.  Two of them in a row doesn't prove anything though.  If you are sure I am with you and thanks. 

Daytona Pete,

That was a trifle strong. Shocked  Not to mention uncalled for. Embarrassed  The apparent "spirit" of your post will get you banished in short order.   Cry  I hope that doesn't happen to you but be assured it has happend to others. Lips Sealed  All of us try to be constructive and helpful and not take anything personal. Embarrassed  If you ever see me or any other heading twords breaking the law in any way I sure hope you would sound off.

If you read a little further back you would have seen that I have a few cans of R12 in my possession.  Barely enuf for one auto system charge but it should be of value to any HVAC guy.....Like Nick(HVAC contractor) and he is in your neighborhood.  I intended to send him my stash out of simple gratitude for the TONS of help he has been to others and me personally on this board. What goes around comes around...if you know what I mean and I am having some doubts here.  Huh  Although, everybody that is trying to keep you out of poop isn't necessarily your friend and everybody that is trying to get you into the poop isn't necessarily your enemy, it usually follows. Cool

About your request to KMRA....I thought the R stood for "Redneck". Huh  I guess it all depends on where you come from and how you were raised. Grin  I just doubt you are Royalty, is all. Wink As to your request: you will have to chalk off a spot cause from here it appears nearly impossible to discern where that part of your anatomy begins or ends. Cheesy Wink Grin  Now see how much more palatable that sort of talk can be if you include all those cute little symbols and some kind words.  I have seen a lot on this board but you are not only unique in your posting but a "natural" as well.   I hope this clears the air and we can become mutually supportive friends.  All in fun now and know that this is a flat medium and subject to missinterpretation and my post is friendly and well intentioned. Kiss

John
« Last Edit: October 25, 2008, 04:33:01 PM by JohnEd » Logged

"An uneducated vote is a treasonous act more damaging than any treachery of the battlefield.
The price of apathy towards public affairs is to be ruled by evil men." Plato
“We can easily forgive a child who is afraid of the dark; the real tragedy of life is when men are afraid of the light.”
—Pla
Hartley
Hero Member
*****
Offline Offline

Posts: 1217





Ignore
« Reply #13 on: October 25, 2008, 03:47:49 PM »

Uh..Oh.. Shocked Shocked

Somebody let Rudolf the Redneck Reindeer off the harness again....

 Roll Eyes Roll Eyes Roll Eyes Roll Eyes Roll Eyes Roll Eyes
Logged

Never take a knife to a gunfight!
kingfa39
Full Member
***
Offline Offline

Posts: 142





Ignore
« Reply #14 on: October 26, 2008, 08:21:24 AM »

i changed my van and my accord to 134, i simply pulled a vacume and changed the fittings added oil and charged them up, 15 yrs ago, no problems with either. i know they say you need to change hoses and all that, i didnt do it. works for me